Question: I have VFD Danfoss and Siemens PLC connected via profibus. Do I need to use PID block of siemens FB41 to reached the required setpoint for pressure based control? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 2/15/2017 11:35:08 AMNew subject after splitting |
|
2/18/2017 3:25 PM | |
Posts: 8946 Rating:
|
If you need high precision speed AND you have a Speed - Feedback Signal, you may use PID.Otherwise, it is not really necessary. BUT if you use the Inverter for pressure control (i.e. controlling speed of pump), a PID connected to pressure transducer makes a lot of sense. |