5/31/2019 7:43 AM | |
Joined: 12/9/2010 Last visit: 10/8/2022 Posts: 623 Rating:
|
Hi Atul Gupta, Manually add connections for both CPUs in NETPRO. Call comm. blocks for both CPU with diffrent conn. ID. Write logic in PLC that if CPU0 fails, CPU1 comm. block will be active. Otherwise CPU0 comm. block is active. U can use SFC51 for CPU RUN/STOP status info. Hope this helps!!!!!!! |
If you like the comment, rate it (right top) or thank it (left bottom). |
|
1/20/2020 6:56 PM | |
Posts: 100 Rating:
|
Is that the only option !? Can we do in Hardware redundancy ? in TIA Portal , All Profinet VFDs doesn't accept multi-assignment like other profinet I/O Sachinpatke
|
1/21/2020 5:23 AM | |
Joined: 7/14/2016 Last visit: 6/27/2024 Posts: 387 Rating:
|
Hello, Same as Y-link in Profibus, we have Y-switch for Profinet. You have to use it for communicaiton of devices not supporting system redundancy, with H-systems. some sinamics VFDs support system redundancy. see this post. HTH Kbv. |
Last edited by: Kbv at: 01/21/2020 05:27:06Last edited by: Kbv at: 01/21/2020 05:29:36Don't just think in terms of solutions... |
|