10/7/2015 8:16 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1050) |
hi, no, I don´t think you can get the F-Cycle-Time out of F_GLOBDB. This is a protected DB, maybe it is inside, but I didn´t found something about it. Have a look to the excel-sheet in the following contribution. You can calculate your max. cycletime of your F-Application-group whit it. S7-Distributed Safety V5.2 + SP2: Execution Times of the F Application Blocks and F-FBD/F-LAD ElementsAn other way is to calculate it by yourself. Read the time when OB35 is started out of the TEMP-Data of OB35 and get the systemtime after execution of the safety part whit SFC1. Then use the FC34 in IEC-Function-Blocks to subtract this times.hope this helps,regards, |
Last edited by: mopS04 at: 10/7/2015 8:26:55 AMFCK WAR! |
|
10/7/2015 9:03 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1050) |
hi, it isn´t difficult too. You can use SFC1 before and after the F-CALL. It is not recommended to call the F-programm in OB1. It is not forbidden, but it could cause problems. Do they know this? Here you see it in the Manual of S7-Distributed Safety. Rules are on page 87. regards, |
FCK WAR! |
|
10/7/2015 2:17 PM | |
Posts: 8946 Rating: (999) |
That is quite crazy... |