10/19/2023 9:27 AM | |
Joined: 5/6/2022 Last visit: 12/4/2023 Posts: 333 Rating:
Hi Riku1979, Can you try the following? After compiling and downloading VoT to the PLC, press F5 to advance changes at runtime or perform a screen change. This could be the reason for the invalid tag name message. I also recommend that you check that the DB mentioned in the message was set. Best regards!
10/23/2023 11:48 AM | |
Joined: 8/3/2009 Last visit: 12/4/2023 Posts: 11798 Rating:
Hello Riku1979 thanks for your feedback, usually the tag rights should be enough to get access: https://support.industry.siemens.com/cs/de/en/view/109803395 Perhaps you check he basicexample again if you missed something... bye Murof |
10/25/2023 6:26 AM | |
Joined: 5/19/2022 Last visit: 11/16/2023 Posts: 9 Rating:
Hello Murof, I missed only one step from example. I didn't installed PLC's web server certificate as trusted root certificate on my computer. I don't think that is problem. On my test application there were only one iofield and one button. Solution was quite clear. I added file system rights to user and VoT application worked. I took those rights off and application didn't worked. BR Riku |