4/2/2008 2:01 AM | |
Posts: 2661 Rating: (279) |
The message means: The local data requirements for OB35 cannot be calculated since some of the called blocks do not have a reference list. In other words there are some blocks which call other blocks that do not exist in the offline block folder. You can easily check this in CFC cross-reference/Block call Hierarchy, import the missing blocks and recompile. See attachement. AttachmentDokument1.pdf (292 Downloads) |
4/2/2008 6:53 AM | |
Posts: 15 Rating: (0) |
Thank you very much! That helped me a lot. Best Regards Kauppp |
4/2/2008 1:48 PM | |
Posts: 1776 Rating: (95)
|
Hi, see the FAQ. There is the help in 6 languages http://support.automation.siemens.com/WW/view/en/8897007 |