Sir, On the following link below for the Diagnostic Block and Visualization via HMI for AS-Interface
the version we could download is v11sp2 when I upgrade I get 4 warnings in HMI_ASI block stating 27,The sign or the accuracy of the value may be lost.,0,1,6:49:56 PM and 1 warning in ASI_DIAG FB stating 58,When the input parameter '#Start' is written, you do not access the operand that was transferred as actual parameter, but rather only the formal parameter of the block.,0,1,6:49:57 PM
thank you AttachmentASI Warnings after upgrade to v12sp1.zip (754 Downloads) |
3/26/2014 2:13 PM | |
Joined: 7/7/2010 Last visit: 4/21/2025 Posts: 15810 Rating:
|
The data type selected in the HMI and the datatype selected in the PLC do not match perfectly, like word in PLC and int in HMI. That gives the warning about accuracy. If your plc logic uses "start" as an input parameter, how are you using it within the FB? As #start or as YourFBdbName.start, or, not at all? |
science guy |
|