Hello Pedro; Unlike other buses that are loop-powered (Profibus-PA, FF...) Profibus-DP requires that all nodes be locally powered at 24 VDC, so the electronics (especially the line drivers)will all have the required voltage and power. So if your bus is "properly" installed, well-grounded. with Class-A cable and connectors and correct termination procedures, if your segment length is appropriate for the communication speed selected, then voltage drop should not be a problem. By the way, where did you take these voltage measurements (between which pins?), and what instrument (DC voltmeter?). If you feel you need a quickrefresher course on Profibus network installation, you could look at this web-based training prepared by Profibus International: http://www.profibus.com/fileadmin/media/wbt/WBT_Assembly_V10_Dec06/index.html Or you could download some of the pdf available from the same site overviewing Assembly and Commissioning of Profibus networks: http://www.profibus.com/nc/downloads/downloads/profibus-installation-guideline/display/ Hope this helps, Daniel Chartier |