9/4/2012 4:30 PM | |
Joined: 7/7/2010 Last visit: 1/24/2025 Posts: 15558 Rating: (2468)
|
If you have not already checked out Pegaia's tips on web pages in the s7-1200, stop and do that before continuing. If you read it and still have problems, I will state my assumptions and then try to help: 1. Your PLC firmware is updated to 2.2 or you have a new 1214 with FW3.0 2. Your TIA Portal V11 SP2 update 3 or 4 (4 is latest as of this post and suggested) 3. Your project is compiled successfully and downloaded to the PLC and plc is in RUN mode 4. You can go online with the PLC from the same computer you are trying to access via web browser 5. You can successfully ping the plc at its configured ip address 6. You are trying to access via internet explorer 8 or 9 7. Your browser is pointed to http://ipaddressofyourplc, like http://192.168.2.2 Ok, if all those assumptions are correct, can you post a screenshot of your project plc configuration with the web server portion expanded? |