1/9/2017 11:42 AM | |
Posts: 1 Rating: (0) |
Hey! First you need to make sure that your PLC permits remote access in TIA portal (check the attachment) You need to make sure that the communication configurations between the PLC and the router are correctly configured, otherwise your router won't see your PLC (Baud rate, Protocol type etc...) ! Establish the remote connection to the router. Once the tunnel towards the router is established, start TIA and open your project. Right-click on your PLC in the Devices area (1), and select Go online from the sub menu (2). Set your type of PG/PC and PG/PC parameters as shown in (2.png) and that should work. Cheers! Saad Z AttachmentDesktop.zip (211 Downloads) |
1/11/2017 10:47 AM | |
Joined: 1/30/2006 Last visit: 9/16/2024 Posts: 310 Rating: (59) |
In general avoid portforwarding due to Security. The best solution would be a VPN connection. BR. Sven |
BR. Sven |
|
1/11/2017 11:43 AM | |
Joined: 2/24/2015 Last visit: 1/25/2023 Posts: 306 Rating: (78) |
There is a brief description on this page - https://support.industry.siemens.com/cs/ww/en/view/26662448 |
Last edited by: Konstantin_D at: 1/11/2017 11:43:35 AM |
|
This contribution was helpful to1 thankful Users |