4/11/2022 7:28 PM | |
Posts: 257 Rating: (80)
For example, a Modbus station is connected to a SIMATIC S7-1500. The communication is programmed and yet the CPU does not establish a connection to the Modbus station. The status of the module is queried and the result is an error code with the designation 16#80CE. Solution: The error code is output if the HW ID on the module was specified incorrectly. The HW ID can be found in the device view under the tab "System constants". Further information on the system constants can be found in the SIOS portal: What is the significance of the system constants in STEP 7 (TIA Portal) for the S7-1200/S7-1500? Best regards, SIMATIC International Technical Support Hub. |
7/12/2022 2:27 PM | |
Joined: 12/16/2021 Last visit: 8/22/2023 Posts: 126 Rating: (2) |
Hi, when you insert 80CE in search field of the online help/manual, you need to select the proper tag of the results. MB_SERVER calls TCON and 80CE from TCON means "invalid IP address". Here in the forum are already threads regarding 80CE. Use the search function in the communication/networks directory to find them. Refer this post for complete details here Regards
If The Information Helpful, Then Don't Forget Give (To thank ) and Rate It |