Hello S7Mgr Let's get some Siemens related acronyms sorted out first: F = Failsafe (the "F" does NOT stand for"fault tolerant"). S7 CPU'sfor "pure" Failsafe applications are315 F, 317 F, 319 F and 416 F and you'll typcially find these in Machine safety related application (sometimes also called Factory Automation Safety). H = High Availability (aka "Fault tolerant", even though this causes some confusion as it also starts with the letterF). High Availability system are based on a redudant architecture and can have a varying degree of redundancy/availabilty. S7 CPU'sfor High Availabilityapplications are412 H, 414 H and 417 H. Note that Siemens also offers a soSoftware Redundancy based system whcih can be used with 300's and 400's. This is however NOT a "H" system and can also NOT be combined with afailsafe application. F/FH = A combination of the two above (A Failsafe system withHigh Availability/Redundancy, aka "Failsafe and Fault tolerant" to continue the confusion)and you'll typcially find these inProcess safety related applications. S7 CPU'sfor High Availabilityin combinationFailsafe applications arethe same as the same as above (412 H, 414 H and 417 H). And here atwo Siemens related starting point links which have more on this subject: Functional Safety (which divides further into Factory Automation safety andProcess Safety) S7-400 H systems I hope this helps |