7/17/2012 2:40 PM | |
Joined: 9/27/2006 Last visit: 1/25/2025 Posts: 12330 Rating: (2702) |
Hello Mazen; Most of your answer is spot on correct, but I must point out that Profibus PA does not use RS-485 to exchange data. It uses MBP (Manchester coded, bus powered) protocol, under specs for the FISCO model which are the same as used by Foudation Fieldbus. This why a DP/PA coupler (or DP/PA link) is required to communicate with PA instruments fromthe Profibus-DP network. You will find more information and links in the following discussion: /tf/WW/en/Posts/66310 Hope this helps, Daniel Chartier |
This contribution was helpful to3 thankful Users |