Hello saruca; I agree with Umencho's post, but here are afew details to explain why your selected CPU will not allow you to connect 8 panels: From the S7-300 CPUs Technical Specifications manual http://support.automation.siemens.com/WW/view/en/12996906 3.2.3 OP communication Properties OP communication is used to exchange data between operator stations (e.g. OP, TP) and SIMATIC modules with communications capability. This service is possible via MPI, Profibus, and Industrial Ethernet subnets. OP communication provides functions you require for operator control and monitoring. These functions are integrated in the operating system of SIMATIC S7 modules. Technical data of CPU 312C (no model -2DP available) Number of connections: Max. 6 Can be used for · PG communication Max. 5 – Reserved (default) 1 – Configurable from 1 to 5 · OP communication Max. 5 – Reserved (default) 1 – Configurable from 1 to 5 · S7 basic communication Max. 2 – Reserved (default) 0 – Configurable from 0 to 2 So: Number of OP communication connections for CPU 312C: Max 5 (low) Number of OP communication connections for CPU 313C-2DP: Max 7 (low) Number of OP communication connections for CPU 314C-2DP: Max 11
|