Dear my colleagues, Have one thing I am confusing in IMs for S7300 like this: I saw that have one jumper to short circuit between M (0VDC) and PE (earth) in power terminal of IMs. In fact, I don't know clearly what is the purpose of this. But I think it may damage to 24VDC power supply unit if accidentally, the L+ wire contact to PE during commissioning time. Because Power supply now is short circuit of output (L+ and M). Could anyone help me to explain this matter. Special thanks all, P/S: you can find attachment about drawing of IMs Tan.nguyennhat
AttachmentIM153.pdf (264 Downloads) |
6/21/2010 6:52 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308)
|
Hello tan-nn , The jumper should be either, Connected in case you have grounded reference installation which means that the M(0VDC) is not left free and connected to a zero reference which is the functional earth. OR Removed in case you have ungrounded reference installation which means that there's an RC combination (internally in the IM153)between the M (0VDC) and the functional earth. You can read more in SIMATIC Distributed I/O device ET200M manual.
It's not about advantages and disadvantages, it's about what kind of installation you have.
1-Working with live wires is not an easy mistake. 2-As Mr. Ayman said you have to use a multimeter and I personallyrecommend toALWAYS makesure L+ is not buzzering with M before you power up any part ofyour system after any kind of wiring modification**. 3- I don't know what is your CPU but did you know before that all 31X CPUs (not the 31X-C CPUs) have the same jumper (Look at attachment*)and I've never seen it taken out. Did you take it out before?! 4- I recommend to protect your IM153 with 2.5A fuses. 5- You will be still connecting 24VDC directly to zero volt without any kind of impedance which means that your power supply may get damaged if it's not protected. *Attachment has been extracted from SIMATIC S7-300 CPU 31xC and CPU 31x: Installation manual **In the last couple of weeks my colleague was about to lose bunch of fail safe modules (quite expensive) because he relied on a technician with more than 10 years of experience (but he was in a hurry)to connect 2 wires and he didn't check after him. No matter how experience you rely on and no matter how you trust yourself and others, always buzzer L+ with M before powering up because we all make mistakes and none of us is an angle. Best regards. H-H Attachment31X CPUs - M and Earth.pdf (380 Downloads) |
Last edited by: H-H at: 6/22/2010 1:36 PMSmall writing mistake |
|
This contribution was helpful to4 thankful Users |