I have a problem when the drive comes from a switch off. After i have done mark zero with MC Home (i have tried with diferents modes :0,1, 6 and 7), all works ok. I can do move absolute, relative etc.. But when the drive start after restablish and acknowlegde the warnings with the MC_Reset the value of position changes to a different value... (for example from 700 mm to 34mm, there are not a math repetitive). And the tecnology object say that reference is OK but the position is not the same. Why the position of the absolute encoder its not saved... Anybody know a solution about that.??? Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/04/2020 14:11:04New subject after splitting |
|
11/5/2020 3:13 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804) |
Hello, set encoder configuration in TO to "cyclic absolute". 3.7.2.2 Absolute actual value (S7-1500, S7-1500T) https://support.industry.siemens.com/cs/ww/en/view/109766462 |
With best regards, |
|
11/6/2020 1:02 PM | |
Joined: 9/3/2019 Last visit: 7/22/2024 Posts: 2 Rating: (0) |
Thanks . It works perfect |