Hi AutoGen_916067, Check at first the follow FAQ: Which quantity framework must you pay attention to for communication between an S7-1200 or S7-1500 controller and WinCC Runtime Professional? https://support.industry.siemens.com/cs/ww/en/view/98699910 Check the follow issues: 1. Does the ping on the PLC work? 2. Is Simatic Net installed ? Wind is not installed as standard with WinCC. Please start → All programs → Siemens Automation - > Simatic → product notes → Inst. Check software There must be a point SIMATIC NET PC software. 3. Are the connection parameters correct in WinCC ? IP address, access point: S7ONLINE, product family 4. Is the access point of the S7ONLINE (STEP 7) application with the correct network type selected in the PG/PC interface? Under Start → Check → PG/PC interface. If the access point is changed, the computer must be restarted 5. Please check in the TIA Portal under Properties → Protection whether the check mark for "Connection mechanisms" is set. Select S7-1200/1500. Press the right mouse button. Select Properties. Select "Protection" under the General tab Scroll all the way down in the window. The check mark when accessed via PUT/GET communication by remote partners (PCL; HMI, OPV, ...) should be set. Best regards schufri |