6/25/2007 2:49 PM | |
Posts: 60 Rating:
|
well, is it my question is too difficult? |
6/26/2007 2:04 PM | |
Posts: 1275 Rating:
|
Hi, What kind of clients do you have? If you have a Client Without Project the security is configured on the server project and works on the client as well. If you have a Client With Project ( multi-project ) then you need to recreate the settings in the User Administrator on the client. So recreate all the users and access levels. If you wantcentralised security across all clients and servers you can use the Simatic Logon Option for WinCC. You can find more information about this option at http://www.siemens.com/wincc/options and select Simatic Logon from the navigation bar. Best regards, Danielle |
6/26/2007 4:00 PM | |
Posts: 1776 Rating:
|
Hi, have a look at the FAQ http://support.automation.siemens.com/WW/view/en/21979623 and also to the Online help Working with WinCC > Setting Up User Administration > WinCC Options for the user Administration> Option SIMATIC Logon > Notes on Linkage to WinCC/Pcs7-OS Best regards April |
6/26/2007 5:25 PM | |
Posts: 1084 Rating:
|
Thanks for posting Wacky. |