11/5/2008 4:33 AM | |
Joined: 10/7/2005 Last visit: 1/17/2025 Posts: 3030 Rating:
|
Hello Charlie not too sure why you loose your assigned PG-PC interface on the WinCC flexPC. Since you operate twoWinCC flex stations on one PLC make sure to untick "cyclic operation"in theconnection setup of bothflex projects (which can be onecause for your sporadic comms failures). Below is theexcerptfrom the WinCC flex online help concerning this: When cyclic operation is enabled, the PLC optimizes its data exchange with the HMI device. This increases system performance. Disable cyclic mode if you are operating several HMI devices in parallel.
|
Cheers |
|