8/29/2022 12:43 PM | |
Joined: 12/19/2019 Last visit: 4/11/2025 Posts: 5 Rating:
|
I use TIA Portal V15.1 and Wincc Professional v15.1 as seen in the picture. |
9/5/2022 9:29 AM | |
Joined: 2/17/2020 Last visit: 4/23/2025 Posts: 1251 Rating:
|
Hi Gertis_M, As other users commented, I would install the latest Software Update ->Update 7 Also, what version of SIMATIC NET do you have installed on the RT Prof PC and what type of license? The version released for WinCC Professional V15.1 is SIMATIC NET V15.0 SP1. On the other hand, the most basic license allows communication with up to 8 S7-PLCs, and in case of exceeding this number, communication may not work at all or may be unstable. |
A rating will be well appreciated. |
|
This contribution was helpful to
1 thankful Users |
9/9/2022 7:41 AM | |
Joined: 8/3/2009 Last visit: 4/24/2025 Posts: 15350 Rating:
|
Hello Gertis_M there are to different updates, one for engineering Station TIA Portal (LINK) and one for the WinCC Professional Rutnime (LINK). you should install both to get the latest Version of your TIA Version. Bye Murof |
If this Information really helps, you could use the Rate function |
|
12/19/2023 9:29 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating:
|
New question published by KurtM60 is split to a separate thread with the subject Wincc Advanced Doesn't reconnect with PLC. Best regards |