“Simple Samples” are small projects that demonstrate simple features. The target is give a quick overview about the theme and be used as start point for related discussions. Follow there are a short description and the configuration main steps.
Description:
Many applications demands that an alarm would be acknowledge by the PLC or that the PLC receive a status if a message was acknowledged.
In this sample project, an alarm (“Alarm 0 active”) could be acknowledged by setting a variable and its status (acknowledged) could be monitored in other variables.
Requirements: WinCC Professional V13 SP1.
Project with a minimum configuration (stop - See references “WinCC Professional V13 SP1 – Simple Sample: Discrete Alarm”https://support.industry.siemens.com/tf/br/en/posts/135058/).
Principle:
1 – Alarms are defined from Word / DWord variables (trigger variable)
2 – An additional Word / DWord can be set as acknowledge functions (i.e. setting this bits, the PLC sends a command to acknowledge the Alarm in HMI). (Alarm properties → acknowledgment → PLC → Tag/bit)
3 – At same way, other Word / DWord variables bit could be used to send a feedback to the PLC that a alarm would be acknowledged (Alarm properties → status → setting → Tag/bit)
Configuration main steps:
PLC acknowledges a alarm
PLC becomes a feedback of an acknowledged a alarm
References: Manual WinCC Professional V13.0 https://support.industry.siemens.com/cs/br/pt/view/92323076/en
Online helps system WinCC Professional V13.0 SP1 https://support.industry.siemens.com/cs/br/pt/view/109096785/en
FAQ Which VBS information and VBS programming tools are there in WinCC (TIA Portal)? https://support.industry.siemens.com/cs/br/pt/view/59885894/en
Tips and tricks for creating scripts in WinCC (TIA Portal) https://support.industry.siemens.com/cs/br/pt/view/57132412/en
How do you acknowledge alarm messages in WinCC Runtime Professional V11 onwards? https://support.industry.siemens.com/cs/br/pt/view/55622122/en