hello, do you have a winCC rt Runtime project loaded and started? Regards Christoph |
3/21/2019 3:11 PM | |
Posts: 70 Rating:
|
yeah a project wincc runtime is started
|
3/25/2019 4:10 PM | |
Joined: 8/3/2009 Last visit: 4/23/2025 Posts: 15338 Rating:
|
Hello The OPC UA Server always runs if you have installed it and activated the Runtime in the Runtime Installatoin. IF you only start the Runtime in the Simulation mode in the Engineerng System then the OPC UA Server will not run! -> You have to load the Project to the Station with the Runtime Installatoin from the RUntime DVD (as in your Screenshot) then start the Runtime and the OPC UA Server will run automatically. Here are a few examples also witch a WinCC Prof. Server: https://support.industry.siemens.com/cs/de/en/view/63481236 Bye Murof |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |