8/3/2021 10:09 PM | |
Joined: 9/27/2006 Last visit: 4/19/2025 Posts: 12346 Rating:
|
Hello Brian; The CSPs available for WinCC (TIA Portal) are not strictly speaking an upgrade of standard communication drivers, but extensions and tests of existing communication channels to include different controllers that were not covered in the original version of the driver. https://support.industry.siemens.com/cs/ww/en/view/109739698 There are no additional mechanisms to deal with issues in the driver n the CSPs,, such as handling of endian problems, which can be frustrating. Most PLCs give a programmer the capacity of dealing with such issues, and that could be an alternative to using WinCC directly with your transmitter; collect the data inside the PLC with all required corrections and formatting, send the data to the WinCC Professional screens when it is ready. This is generally the way we preferred handling such situations. Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |