5/25/2011 3:55 PM | |
Joined: 1/17/2006 Last visit: 4/16/2024 Posts: 800 Rating: (63) |
starting up in save mode? Is it possible? |
This contribution was helpful to1 thankful Users |
5/26/2011 7:40 AM | |
Joined: 10/3/2010 Last visit: 5/24/2024 Posts: 1552 Rating: (188) |
that's quite hard when the screen is showing only 'signal out of range' resetting under safe mode or auto-button are the ways to go. |
B r g d s , |
|
5/26/2011 9:00 AM | |
Joined: 10/3/2010 Last visit: 5/24/2024 Posts: 1552 Rating: (188) |
it's like the original post said, it happened after an operator changed the resolution, so it's quite clear he was able to set a resolution (instead of testing first )that the screen can't display. |
B r g d s , |
|
5/26/2011 12:36 PM | |
Joined: 10/3/2010 Last visit: 5/24/2024 Posts: 1552 Rating: (188) |
glad that it's solved but in worst case scenario, after power off (if no other way, keep power button pressed), you should be possible to get into safe mode on next boot. btw, thw Komi for the other idea's |