Hey Murof, i have 16 s7-1200 PLC's connected on profinet network,with a PC which has Wincc RT Advanced 128 powertag software. Everything works perfectly but certain IO field start showing ### after a certain time when Wincc RT is switched on . Would you please suggest some solution for this, i also pinged the ip's of all PLC they are all echoing back. I can't think of any other solution so please help!! Would appreciate.. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 3/29/2018 8:58:33 AMNew subject after splitting |
|
3/28/2018 6:54 AM | |
Joined: 9/20/2014 Last visit: 7/18/2024 Posts: 56 Rating:
|
hi check MAC address in Wincc setting , should be match with CP (Ethernet) |