3/7/2022 10:07 PM | |
Joined: 2/17/2020 Last visit: 4/23/2025 Posts: 1251 Rating:
|
Hello Fakhar Abbas, If it is a WinCC Professional SCADA architecture with a server and a client, and you do not want someone to be able to operate on the WinCC client, you should define a user in the Runtime, which is within a user group that only has monitor permission. Then, in the client, when this user logs in to the Runtime of the project, he will not be able to handle the controls, but only view the contents of the configured screens. Maybe this application example will be useful: User Administration in WinCC (TIA Portal) |
A rating will be well appreciated. |
|
3/10/2022 2:28 PM | |
Joined: 1/29/2021 Last visit: 1/31/2023 Posts: 8 Rating:
|
Yes, I did the same thing. I only check two authorization (Monitor and Enable Remote Control) for my WinCC Client. The client can also log in on the Client's PC but can also operate in Runtime. I only add one toggle button and one circle on the screen. He can operate (toggle) the button. What could be the reason? AttachmentWinCC_Server_Client_Configuration.zip (382 Downloads) |
Last edited by: Fakhar Abbas at: 03/10/2022 14:29:09Last edited by: Fakhar Abbas at: 03/11/2022 11:15:37 |
|
4/18/2022 7:41 AM | |
Joined: 1/29/2021 Last visit: 1/31/2023 Posts: 8 Rating:
|
Now, all issues have been resolved. |