Hi, I am using WinCC Fexible 2008 SP3, Build V1.4.0.0_1.16.0.7 with windows 7 x86 SP1. |
7/30/2018 10:38 AM | |
Joined: 8/3/2009 Last visit: 3/27/2025 Posts: 15107 Rating:
|
Hello First of all I would try to use UPdate 7 for WinCC Flexible 2008 SP3 on Engineering system and Runtime System. There are years of improvement into the Updates. Perhaps it has an effect on your Problems. https://support.industry.siemens.com/cs/ww/en/view/58860033 Bye Murof |
If this Information really helps, you could use the Rate function |
|
7/30/2018 1:29 PM | |
Joined: 2/7/2017 Last visit: 6/26/2023 Posts: 10 Rating:
|
Hey! I tried installing the update 7 pack but nothing happend about my problem. Anyway i found the solution. When you create tags, with the plc connection you have the property : Aquisition mode : Cyclic continuous with Aquisition cycle : 500 ms . If you set it like this it will reconnect automaticly after a reestablished connection . Mine was set on cyclic on use and got stuck like that. |