1/19/2018 4:32 PM | |
Joined: 4/24/2006 Last visit: 2/14/2025 Posts: 8848 Rating:
|
Hello, did you transfer the license to the panel? Best regards, Wizard |
1/22/2018 8:29 AM | |
Posts: 32 Rating:
|
Hello, No i did not. I did put it to the local disk? Isn't that right? |
1/22/2018 8:45 AM | |
Joined: 9/21/2012 Last visit: 2/11/2025 Posts: 4278 Rating:
|
It needs to on the Panel, not the PC. |
1/22/2018 8:45 AM | |
Joined: 4/24/2006 Last visit: 2/14/2025 Posts: 8848 Rating:
|
Hello, You have to tranfer the Sm@rtServer license to the panel. You can use Automation License Manager: Remote Access to SIMATIC HMI Control Panels See the document "Documentation Sm@rtserver" See chapter 4.2.3 Best regards, Wizard |