Hello be sure that the limits for an Advanced Runtime are max. 500000 Entries per Log If you have segmented Logs then you have to calculate the product so for example 50000 entries and 10 Segments are -> 500000 entries per Log(the maximum!) and so it is also written in the Help System! In Comfort panels the Limits are much lower -> depends on the size from 20000 to 50000 -> if you need more have a look at this Workaround or use WinCC Professional RT (another System with SQL Server inside, here you can use much,muchmuch more data) https://support.industry.siemens.com/cs/de/en/view/109477071 Bye Murof |