Joined: 6/8/2007 Last visit: 10/24/2024 Posts: 54 Rating: (3) |
Hi all, I have a setup with 12 S7-1200 PLCs (CPU1215 DC/DC/DC) all connected to a PC with WinCC RT Advanced V13 SP1 running on Windows 7 Professional. In TIA I have set up 12 HMI connections, one for each PLC, none of them shows any problems in the configuration. My project compiles just fine. Still, when I physically connect all of them, two of my PLC will not display any process values, just #### as if the PLC is not connected to the network. If I disconnect any two PLC from the Ethernet switch, all the others are on-line and visible in WinCC RT. It looks as if the maximum number of online HMI connections at a time is 10. But I'm not sure about this, and all I could find about it is this:
see this link: https://mall.industry.siemens.com/mall/en/WW/Catalog/Products/10093867?tree=CatalogTree under Product Information. Now what exactly does connection based on "SIMATIC HMI HTTP" mean? Any ideas somebody? Thanks, Boti |
||||
Last edited by: jboti at: 11/11/2015 8:16:57 AM |
|||||
11/11/2015 8:19 AM | |
Joined: 5/12/2006 Last visit: 12/7/2024 Posts: 22474 Rating: (3037) |
Hello, the SIMATIC HMI HTTP Connection is a Communication protocol. The SIMATIC HMI HTTP protocol is a constituent part of the Sm@rtAccess option. https://support.industry.siemens.com/cs/ww/en/view/18797552 Regards Christoph |
This contribution was helpful to1 thankful Users |
11/11/2015 8:29 AM | |||
Joined: 6/8/2007 Last visit: 10/24/2024 Posts: 54 Rating: (3) |
Hello, Thanks CristophD, so this doesn't count for my problem. That leaves me with the option:
which is still strange, because TIA will let me configure 12 HMI connections, and RT certainly handles 10 active connections at a time. But why not 12? Cheers, Boti
|
||
3/30/2017 1:24 PM | |
Posts: 14 Rating: (3) |
It seams to be 16 HMI connections in WinCC RT Advanced V13. Look the picture. |