Hi, “Simple Samples” are small projects that demonstrate simple features. The target is giving a quick overview about the theme and be used as start point for related discussions. Follow there are a short description and the configuration main steps. Despite of all diagnostic resources of TIA, sometimes it is interesting have a bit that shows to the HMI if the PLC is running ok or, a bit to that shows to the PLC that the HMI/SCADA is running. Depending on the case, this bit should not show if the communication is ok, but also that informs that the programing is running and running in a specific condition (e.g. “not hanged”). This type of the monitoring is donning e.g. by a live bit (some signal that changes on the time to prove the health of the system). In this simple sample, there are two live bit monitoring: one from controller to HMI and other from HMI to controller. In both cases an integer variable is incremented and the partner checks if it changes during a time interval. As result an OK bit is generated. In the PLC it is done by a single block. In the WinCC Unified (as didactical proposes) is done by two separate time triggered schedule tasks. Sample project archived and zipped. AttachmentliveBit.zip (690 Downloads) |
Denilson Pegaia |
|
This contribution was helpful to1 thankful Users |
7/10/2023 10:15 AM | |
Joined: 9/23/2005 Last visit: 9/19/2024 Posts: 4347 Rating: (1446)
|
TIP: To see the CPU status (RUN, STOP) see also the post WinCC Unified – Simple Sample – Communication live bit monitoring |