10/22/2017 8:41 PM | |
Joined: 9/27/2006 Last visit: 1/25/2025 Posts: 12331 Rating: (2702) |
Hello Tekabi; This discusion should give you and idea for wibre break detection: a sunt resistance near the field connection, with a diagnostic interrupt activation. The discussion was about S7-300 hardware, but should be applicable to your situation. https://support.industry.siemens.com/tf/WW/en/posts/di-wire-break-issue/88867?page=0&pageSize=10 Hope this helps, Daniel Chartier |
12/19/2024 6:46 AM | |
Joined: 11/11/2024 Last visit: 1/14/2025 Posts: 1 Rating: (0) |
Hello Tekabi, can I use wire brake function in profinet and profibus communication?That mean went I take out one of the profinet cable from device, it will be appears alarm.
|
Last edited by: farihin_fauzi77 at: 12/19/2024 06:46:40 |
|
12/28/2024 8:29 PM | |
Joined: 9/21/2012 Last visit: 1/25/2025 Posts: 4264 Rating: (479) |
You can use DeviceStates instruction to detect if a configured Profinet or Profibus node is missing from the controller. |