12/27/2013 1:06 PM | |
Joined: 8/16/2010 Last visit: 4/24/2024 Posts: 636 Rating: (12) |
Hi all... I need help about wiring valve actuator (input voltage-24 VAC, input signal: 0-10V) with SM1232 AQ4... In attachment is eplan diagram (which I maked) and specification of the actuator. So, to supply actuator I need transformer 220/24VAC. One output wire of transformer is connected to COM of actuator, and 0M of the module (viev attached eplan). Another wire of transformer is connected to 24VAC. And 0 terminal of module is connected to signal Y of the actuator. Is this good diagram??? AttachmentEPLAN.pdf (288 Downloads) |
Last edited by: Milosh at: 12/27/2013 1:06 PM |
|
12/27/2013 1:07 PM | |
Joined: 8/16/2010 Last visit: 4/24/2024 Posts: 636 Rating: (12) |
Specification of actuator...
Attachmenten0b0097-ge51r0513.pdf (302 Downloads) |
1/3/2014 8:26 AM | |
Joined: 8/16/2010 Last visit: 4/24/2024 Posts: 636 Rating: (12) |
Hi...koenb Thank's for reply but I can't download from link you posted in priv. message. Can you share it here, please? |
1/3/2014 8:39 AM | |
Joined: 6/26/2009 Last visit: 4/25/2024 Posts: 122 Rating: (23) |
as requested..
AttachmentAC-Servovalve.pdf (289 Downloads) |
This contribution was helpful to1 thankful Users |