1/9/2015 4:55 PM | |
Posts: 23 Rating: (0) |
Dear Hristo, The RTD is Pt100 type in 4 wire configuration and I haven't measured the resistance between the leads yet. Regards, Ankur Gajjar
|
1/9/2015 5:33 PM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2683)
|
Hello Ankur; What position have you set the range module for your channel group? Look on the side of the module (you must remove it from the connection rail); it should be on "A" for 4-wire RTD measurement. See the following attachment from the S7-300 Module Data manaul. Also look at the note at the bottom of the screencapture, you are getting a 7FFF(Hex) value in your measurement... S7-300 Module data manual - Siemens Hope this helps, Daniel Chartier |