8/18/2022 1:13 PM | |
Joined: 10/11/2006 Last visit: 10/18/2024 Posts: 5924 Rating: (810)
|
Dear s27, A501 is triggering the Imax controller. If the overload condition couldn`t be solved F1 is triggered, see picture attached of the V20 operating instruction manual chapter 5.6.2.7. Unlike the SINAMICS G and S drives, which have p2128/p2129 to generate a trigger bit based on active fault or warning messages, the V20 doesn`t have those kind of parameters available. |
With best regards, |
|