Siemens always recommends to update to the latest firmware where possible. Your V2.1.x CPUs can only be updated using a 4MB memory card according to the procedure at the link below: https://support.industry.siemens.com/cs/de/en/view/18722504 However, in the STEP 7 V5.x hardware catalog, only the firmware V2.1 exists, and there is no 3 digit firmware. So technically, yes, you can exchange the V2.1.3 <=> V2.1.8 CPUs. |