6/12/2012 7:45 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, You see no leds because there are no leds. Paw is o.k. if you program in German, in English it is PQW. You can send value to PQW(and monitor) by using a MW L mw100 T pqw512 In mw 100 you can now put your value by VAT. Sure you connected the power to the module? No errors in diagnostics? Attached you find the Module data and connection diagram. Regards, Marcjan Attachment6ES7432-1HF00-0AB0).pdf (285 Downloads) |
Problem solved? |
|
6/13/2012 9:54 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, There are so many connectors because voltage and current outputs have own connectors. I have attached a schematic to wire current outputs, note wire bridges and all m-ana need to be connected together. For the first channel: Bridge 6+7 7= analog out + 8= analog out - Regards, Marcjan Attachmentanalog-out.pdf (315 Downloads) |
Last edited by: Marcjan at: 6/13/2012 9:55 AMProblem solved? |
|