2/17/2020 5:47 AM | |
Joined: 5/18/2012 Last visit: 5/5/2024 Posts: 3 Rating: (0) |
Hi Christoph. Are Profinet connected devices restricted to this default process image size? I have a 1215c that is used just for profinet control to collect flow meter data. Each sensor has 94 bytes of input and 3 byte of output and I get an error when I add the tenth sensor. Thanks, ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/17/2020 07:42:56New subject after splitting |
|
2/17/2020 6:19 AM | |
Joined: 5/12/2006 Last visit: 10/18/2024 Posts: 22422 Rating: (3023) |
hi, no restriction. all devices are in the process image. Regards Christoph |