1/4/2021 2:37 PM | |
Joined: 4/9/2009 Last visit: 5/3/2024 Posts: 64 Rating: (1) |
Hi, I want to monitor a state of motor and store retentive:
About point 1 to 5 there are no problem (see attachment) but I dont understand how store the Hour activation yesterday. Is it possibile? Another question about Hour counter:
Thansk and Best Regards AttachmentTest Counter Forum.zip (97 Downloads) |
1/4/2021 4:49 PM | |
Joined: 12/27/2006 Last visit: 5/23/2024 Posts: 1196 Rating: (113) |
Yes, the Hourcounter counts only hole minutes. If its a problem use one of this counters. The first counts hole seconds, and if that not enough, the second counter counts 0,1 sec. AttachmentUrenteller.zip (109 Downloads) |
1/4/2021 5:09 PM | |
Joined: 12/18/2014 Last visit: 5/26/2024 Posts: 33108 Rating: (4087)
In attachemt a possible solution for storing runtime of yesterday. Take a look at the Parameter-VM-Mapping. The counter value is a DInt. Values smaller 32.768 are in the right word of the DWord (in example VD0). The right word is VW2. AttachmentStoring_runtime_yesterday_8.3.zip (122 Downloads) |
This contribution was helpful to1 thankful Users |