11/21/2019 8:23 AM | |
Joined: 9/9/2015 Last visit: 4/11/2024 Posts: 727 Rating: (268) |
Dear paresh_ramdya, Are you able to open the module information of the PLC? the Rack 1 PLC. Look for the "Stack" tab. It can show you what is stopping the plc from booting up. But i guess you cant open the module information. Normally I caused by something wrong with programming. Memory reset the second CPU, (PLC->Clear/reset, or manually force reset at local) , then turn on the CPU again and download the CPU again. Check your modified program, any special DB/FB/SFB you have override, you can also restore back the previous working one to study the behaviour. Hope it is helpful for you |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
11/22/2019 7:09 AM | |
Joined: 10/9/2018 Last visit: 4/30/2024 Posts: 26 Rating: (0) |
make sure your LAD/STL/FBD is closed when you try to put them in run |