6/24/2009 1:52 PM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
Yes. The system will work as "Single-channel, one-sided I/O system"
No. Only when CPU0 is available (and in run mode - master or standby), then CPU1 will have access to IO modules in rack 2 and rack 4.
No. Nothing else is required except the 2 sync cables. I would suggest reading chapter 10 ofthis manual. This should solve all your doubts.
|
This contribution was helpful to1 thankful Users |
7/2/2009 8:45 AM | |
Joined: 7/2/2008 Last visit: 5/16/2024 Posts: 928 Rating: (306) |
Hello Kareto, For one sided switched I/Os you need to buy what so called Red. Bundle for each distributed rack. The Red bundle has a single part number but comes with three parts. two of IM153-2 and a single active busmodule (IM/IM)(Active back plane). In Hardware configuration you won't find Red. Bundle and you will just find IM153-2. However, you will find the DP slave connected to both DP Masters. Take care because you also need active busmodules for signal modules. To know the count and part numbers you require, Please go to slave properties in HW configuration and check operating parameters. Best regards. H-H |
7/2/2009 11:35 AM | |
Posts: 16 Rating: (0) |
Thanks H-H and one more question. Can I useoneIM 153-3 with 2 DP portsinstad of Red. Bundle with 2 IM 153-2 s? |
7/30/2009 3:34 PM | |
Joined: 11/8/2006 Last visit: 5/8/2024 Posts: 57 Rating: (4) |
Dear All, I wanted to make a system with CPU as well as signal module redudant.I made configuration(attachment).But some how I am able to make only CPU redundancy not signal module redundancy.When I am checking property of signal module(Digital Input),redundancy tab option is not coming. What need to be done? Thanks and regards. Ambrish AttachmentRedundan.zip (323 Downloads) |
7/30/2009 8:22 PM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
The module 6ES7321 1BL80 0AA0 does not support IO redundancy. That's why you don't see the tab redundancy. For a complete list of modules that support redundant IO operation please refer the table 10.2 (pg 137 to 143) inS7400H Fault taulerant system manual. (edition 2/2009)
|
7/31/2009 2:24 PM | |
Joined: 11/8/2006 Last visit: 5/8/2024 Posts: 57 Rating: (4) |
Thanx for your answer.Now please look at attachment .Now I tried with MODULE mentioned in the manual.Same problem again.I am doing some mistake!But I am not able to find it out. Please have a look and let me know where I am wrong. Regards Ambrish. AttachmentRedundan.zip (251 Downloads) |
7/31/2009 6:50 PM | |
Joined: 7/2/2008 Last visit: 5/16/2024 Posts: 928 Rating: (306) |
Hello ambrish, I opened yourproject and couldn't configure redundancy for that module. However when I created a new project, I could configure redundancy. It seems to me it's a matter of versions and service packs so I hope you have STEP7 V5.4 with latest service pack. I also find it better to test my configuration on your ES if you already have the latest version and latest service pack. Best regards. H-H AttachmentTest_Red_IO.zip (246 Downloads) |
8/1/2009 6:39 AM | |
Joined: 11/8/2006 Last visit: 5/8/2024 Posts: 57 Rating: (4) |
Thnaks |
8/1/2009 9:42 AM | |
Joined: 11/8/2006 Last visit: 5/8/2024 Posts: 57 Rating: (4) |
Can you send any sample project(program) with I/O redundancy? Thanks Ambrish. |
8/3/2009 4:05 PM | |
Joined: 3/18/2009 Last visit: 5/6/2024 Posts: 306 Rating: (94) |
It's correct. The modules will always have different addresses. However, you have to use only the lower adresses in your program. I don't have a sample program, my be someone will help you with that. I would suggest reading the help of the redundant IO library blocks. They are pretty much what you need to understand and configure IO redundancy. Just couple of quick tips,
|
Last edited by: daga at: 8/3/2009 4:08 PM |
|