11/28/2012 12:12 AM | |
Joined: 2/10/2006 Last visit: 3/21/2024 Posts: 147 Rating:
|
you can use the CTI 2500-RBC Profibus DP remote base controller. http://www.controltechnology.com/products/2500-rbc/ it allows you to connect TI545 bases to an S7 CPU and configure them as Profibus I/O on the S7 CPU.The CTI 2500-RBC is fully compatible with the TI545 I/O and bases. The GSD file can be downloaded from the Controltechnology.com website. Regards, |
11/28/2012 12:13 AM | |
Posts: 510 Rating:
|
Colbain, Yes you can use the 505 Profibus RBC and SIMATIC TI I/O modules. In the hardware catalog, under Compatible Profibus DP slave in the folder SIMATIC, you will find the 505-6870 DP RBC with the I/O. If you have I/O in the CPU rack, you can remove the 545 CPU and replace it with the 505-6870 to use the I/O. As for the 505-6851, theywill also have to be replaced with the 6870. Last I checked, Siemens still has these in stock.If Siemens does not have them currently, you can try Control Technology Inc, in Knoxville, TN. Here is a link to their product bulletin. ftp://ftp.controltechnology.com/public/Pubs/PRODUCTS/2500-rbc/2500RBCbulletin.pdf I have attached a white paper Idid on converting 505 to S7 Good Luck, billwest AttachmentSimatic 505 Migration White Paper.pdf (709 Downloads) |
10/8/2014 10:46 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating:
|
|