3/27/2012 12:32 AM | |
Joined: 6/15/2010 Last visit: 2/18/2021 Posts: 31 Rating: (1) |
Hi, We urgently need technical assistance from Siemens to confirm the following : 1) Attached configuration with S7-400 H-system and remote IO is feasible. 2) Confirm that Compressor system 2 can still immediately operate if Compressorsystem 1 is de-energised (ie: No power to Compressor skid 1 RIO rack and Compressor skid 1 OLM). The opposite case for Compressor skid 2 de-energised should also be confirmed. Let me know in case of any Qs. Regards, D AttachmentFibre Option 3.pdf (483 Downloads) |
3/27/2012 6:56 AM | |
Joined: 10/7/2005 Last visit: 5/8/2024 Posts: 3004 Rating: (1046)
|
Hello dshha here's my take on things:
It looks like a rather "odd" PB design at first glance, but itwill - in principle - work
It may is the best answer I can give you, andyou shouldbe aware of the following: - As already stated by Aret, you'll loose proper Segment termination, which may lead to a loss of the other compressor systems RIO rack too. The only way to avoid this is by adding a copper Profibus return line from each skid back tothe other skid and placementof active Profibus terminator there (and ensuring to notexceed permissible Segment lenght) - You will loose the Profibus redundancyand now operate the remaining Compressor RIO rack on a single Profibus/IM153. Opting for a dual redundant FO Profibus will eliminate the above issues and would be my personal Design choice and attached is a sketch on how it would look I hope this helps |
Cheers |
|
3/27/2012 7:59 AM | |
Joined: 6/15/2010 Last visit: 2/18/2021 Posts: 31 Rating: (1) |
Hi fritz and Arit, AttachmentFibre option 3 rev1.pdf (492 Downloads) |
4/23/2012 12:46 AM | |
Joined: 6/15/2010 Last visit: 2/18/2021 Posts: 31 Rating: (1) |
Thank, Could you please prepare the drawing for me. I appreciate your help with this. Regards, D |
4/23/2012 9:35 AM | |
Posts: 947 Rating: (45) |
Hi! I believe that the Hw-config should specify the use of optics in the profibus. This is something discussed in the Faq Support. |