5/11/2020 6:32 PM | |
Joined: 7/15/2008 Last visit: 1/23/2024 Posts: 382 Rating: (44) |
Hello. What seems odd to me here is the following, You have a H system with 2 independent Power supplies and 2 independent PLC,s and you are loosing the PLC program of both ??? PLC,s when you turn of the main supply and both PLC's are going through their startup / diagnostic routine. If the backup battery's are ok on both PLC's, and you have not an issue with the back-plate connection, I don't see how his can happen. Also your Firmware is 4.0, but what what revision. The current revision is 4.0.12. Please ensure you have the latest Firmware on both PLC's. https://support.industry.siemens.com/cs/us/en/view/109474747 You can also contact Siemens Support for some more help. Regards / m.f.g |
Last edited by: legacy support at: 05/11/2020 18:38:56Last edited by: Jen_Moderator at: 05/12/2020 08:53:19Optimized link. |
|
5/12/2020 2:42 AM | |
Joined: 11/28/2015 Last visit: 6/29/2023 Posts: 5 Rating: (0) |
The Firmware is V4.0.9 Very grateful for the help. |