The ordered drive is 2Q & as such you can not achieve/run motor in both the directions i.e. forward & reverse. With this drive, if you want to run motor in both directions, you need to incorporate relay logic in order to reverse field voltage & tacho feed back polarity with proper interlocks. (Please refer attached circuit for more information) Please note with this arragentment you can not achieve motor braking application. If you want to run motor in both directions without relay logic & motor braking application then you need to select 4Q drive i.e. 6RA8093-4DV62-0AA0 Attachment6RA 80 2Q field reversal.pdf (430 Downloads) |