7/23/2019 11:44 AM | |
Joined: 5/12/2006 Last visit: 10/15/2024 Posts: 22414 Rating: (3017) |
Hi, 2.) is specified in PROFINET Specification (https://www.profibus.com/) 3.) do you know what you do? Do you know what the attributes in the GSDML mean and how they work? 4.) 315-2EH13 is old outdated PLC with old PN Stack (V2.1) which not support newer PN standards Have you check you modificated GSDML in the GSDML Checker? Christoph |
7/23/2019 1:51 PM | |
Joined: 5/12/2006 Last visit: 10/15/2024 Posts: 22414 Rating: (3017) |
hi, most changes can be read in the delievery notes of the PLC https://support.industry.siemens.com/cs/ww/en/view/38727042 here you can see that there major changes for PROFINET are made, same information you get from delievery notes of new FW Versions for the PLC.
Christoph |
7/24/2019 3:46 AM | |
Joined: 8/13/2018 Last visit: 2/22/2024 Posts: 51 Rating: (0) |
Hi Christoph, 1. I referenced the page you provided and I still can not find PN Stack Version of PLC you mentioned. I can see new function note, Step 7 version and PLC firmware version, but not PN Stack Version. 2. Could you kindly tell me what is the file name which record "slot 0 can not be set I-Device" ? https://www.profibus.com/download/
Very appreciate for your help. |
9/3/2021 9:01 AM | |
Joined: 1/9/2020 Last visit: 11/1/2023 Posts: 7 Rating: (0) |
Hello Where can i find it in old step 7? |