5/9/2012 7:51 AM | |
Posts: 18 Rating: (0) |
active or passive able in 6es7331-0kf02-0ab0 |
5/9/2012 8:13 AM | |
Posts: 139 Rating: (5) |
Hi, Do u means 4 wire or 2 wire current configuration input? |
5/9/2012 8:18 AM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, Are you sure about that number? Maybe you mean the 1KF02? See attached module data. Regards, Marcjan Attachment1kf02.pdf (174 Downloads) |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
5/9/2012 8:23 AM | |
Joined: 9/28/2005 Last visit: 8/27/2024 Posts: 2957 Rating: (242)
|
Do you mean 6ES7331-7KF02-0AB0 ? Look in this manual SIMATIC S7-300 S7-300 Automation System Module Data chapter 6.7 page 345 for 2 or 4 wire connection. |
Best regards, |
|
5/9/2012 8:25 AM | |
Joined: 9/28/2005 Last visit: 8/27/2024 Posts: 2957 Rating: (242)
|
I thought of 7KF02 |
Best regards, |
|
5/9/2012 8:27 AM | |
Posts: 1064 Rating: (72) |
take a look at this manual it should help with all your questions start at page 357 http://support.automation.siemens.com/WW/view/en/8859629 |
5/9/2012 10:41 AM | |
Joined: 4/24/2006 Last visit: 10/18/2024 Posts: 8746 Rating: (1169) |
Hello, Both cards (7KF02 or 1KF02) is it possible to connect active or passive components. If you have 7KF02, see earlier mentioned manuals. And if you have 1KF02 have a look in manual and see also: how do you connect a 2-wire measuring transducer to analog module 6ES7 331-1KF0.-0AB0 a compact CPU or a C7 device? Best regards, Wizard |
This contribution was helpful to1 thankful Users |