7/6/2012 10:17 AM | |
Joined: 9/6/2008 Last visit: 5/7/2022 Posts: 1121 Rating: (86) |
Hi Furthermore if you have used the error OB then it will tell you the address of the fault. Have fun... |
Jazz |
7/6/2012 5:40 PM | |
Posts: 36 Rating: (0) |
DearTagolover Yes this address has been shown in "OB121_PRG_ADDR" interface of "OB121", and this address refers to instruction whitch has generated the fault, but i mean what is the relation between this number and actual position of the nstruction whitch has generated this error? Best regards Ali. |
7/6/2012 7:05 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hello , It is better to consult STEP7 online manual (See the attachment). OB121_PRG_ADDR : WORD --> Relative address of the MC7 command that caused the error (no valid value is entered here for an S7-300) LAD/STL/FBD editor converts your logic to MC7 codes. As far as I know,MC7 is known for the editor and this guide you to point of error in case of error. Best regards Hamid Hosseini AttachmentOB121.pdf (953 Downloads) |
7/7/2012 12:09 AM | |
Dear Mr. Hamid Hosseini Thanks for your explanation,my question has been answered completely. Good luck
This contribution was helpful to1 thankful Users |
7/7/2012 8:35 PM | |
Dear Mr.Hamid Hosseini Is there any way to determine relative address of any instruction in a block? Thanks Ali
Follow us on