9/5/2008 7:45 AM | |
Joined: 10/31/2005 Last visit: 6/12/2024 Posts: 360 Rating: (31) |
Most likely, you'll need to download the program agian. Please, have a look at this thread to learn what is overall reset: /tf/WW/en/Posts/21014#top |
Last edited by: Pandiani at: 9/5/2008 7:45 AM |
|
9/5/2008 8:15 AM | |
Posts: 3 Rating: (0) |
Thank you for help |
9/5/2008 9:00 AM | |
Posts: 133 Rating: (9) |
Hi Ildar Ssc_Mikro is right BASP means that the outputs are disabled. You would have to reload the program via a programming unit with Step 5 of you would have to use an EPROM or EEPROM with the correct program. Cheers AttachmentBASP S5 942 CPU.pdf (119 Downloads) |
9/6/2008 1:56 PM | |
Posts: 94 Rating: (15) |
Hi Ilder I think no progarmme available in the CPU. If you have a programme backup then through step-5 software you can download the same. Regards :- Titas |
9/21/2008 1:37 PM | |
Posts: 133 Rating: (9) |
Hi Ildar Is your problem solved? |
10/4/2008 4:56 PM | |
Posts: 3 Rating: (0) |
Thank you for posting Bilal. I reloaded the program, butnewledappeared"ZYK". Do not know what to do. At the momenttryingtostudyS5. |
10/5/2008 6:15 PM | |
Posts: 133 Rating: (9) |
Hi Ildar Check out the attatched document. This is from the manual. Cause Scan time exceeded: The program scanning time is greater than the set monitoring time.Remedy Check the program for continuous loops. If necessary, retrigger the scan time with OB31 or change the monitoring time. AttachmentZYK.pdf (122 Downloads) |