9/21/2009 9:26 AM | |
Joined: 4/24/2006 Last visit: 9/26/2024 Posts: 8742 Rating: (1168) |
Dear IvanG, I think, you will have to use a compare function in PLC. There you set a bit, which can be assigned to an Alarm message. Within this Alarm message, you can show the value of Analog tag. Perhaps this link, might help: http://support.automation.siemens.com/WW/view/en/5155755 Best regards, Wizard |
9/21/2009 3:34 PM | |
Posts: 6 Rating: (0) |
That's it. Thanks a lot. |