4/19/2009 1:19 AM | |
Joined: 7/2/2008 Last visit: 5/16/2024 Posts: 928 Rating: (306) |
Hi Alindsay, Are you sure this error in reading represents a problem for you? I don't know which module you are using. I knowthat1KF01 module has an error of+ or -1 K. I don't think other modules would have much muchless error. check your module error in S7-300 module data. I believeyour smallerror will be inmodule operational error limit. PT-100 errors appear when cable resistance is considerable specially if you are connecting PT-100 using only 2 wires. When you have considerable cable resistance, you might need to subtract cable resistance from actual reading but if you are talking about errors that lies inside module operational error limit, I don't think there's something to do. I hope someone with more experience can give you a solution. |
4/21/2009 11:58 AM | |
Joined: 5/28/2008 Last visit: 5/20/2024 Posts: 4506 Rating: (836) |
Hello, Did you thought to use PT1000 instead of PT100 for your application. PT1000 will give you higher precision and I think you can reduce the error 10 times. 10 times because, the value of the resistance at certain temp. with PT1000 =the value of the resistance at same temp. with PT100 MULTIPLIED by 10. Here's attached tables for both PT100 & PT1000 vs. temperature. With best regards, AttachmentRTDs.zip (581 Downloads) |
Last edited by: Ayman Elotaify at: 4/21/2009 12:00 PMAyman Elotaify |
|
4/29/2009 3:02 PM | |
Joined: 4/24/2008 Last visit: 5/16/2024 Posts: 209 Rating: (16) |
I think this FAQ will help you toqualify your measurement. http://support.automation.siemens.com/WW/view/en/26116994 |
|
|
This contribution was helpful to1 thankful Users |